Limit Switch Grounding

Discussion in 'General Talk' started by Trevor Farnum, Mar 27, 2023.

  1. Trevor Farnum

    Builder

    Joined:
    Feb 15, 2017
    Messages:
    57
    Likes Received:
    10
    I've searched so many threads, with so many different opinions on grounding, creating a grounding loop or not, etc.

    Long story short, I'm hoping someone can tell me which diagram is right (my bet is on A). I'm running 3-wire shielded (2 wire would have probably worked too), to the NO and C. I'm trying to figure out how to ground the shielding correctly. I understand the BlackboxX32 has built in capacitors, so I don't need to add in any ceramic capacitors. If that is wrong, please let me know if I need to add in a 0.01UF ceramic capacitor to the GND/SIG. I also don't think I should be doing anything with the shielding at the end other than cap it off - but I do have a spare wire if I needed to connect that to bring it back to ground. IDK, so many people saying so many things - what does our community say?

    Option A - I believe this is right:

    upload_2023-3-27_19-44-46.png


    Option B - With Capacitor:
    upload_2023-3-27_19-56-54.png


    Option C - No Capacitor but ground pulled from end:
    upload_2023-3-27_19-57-39.png


    Option D - Do everything, because why not:
    upload_2023-3-27_19-58-20.png
     
  2. Peter Van Der Walt

    Peter Van Der Walt OpenBuilds Team
    Staff Member Moderator Builder Resident Builder

    Joined:
    Mar 1, 2017
    Messages:
    14,868
    Likes Received:
    4,283
    Option E is preferable: Xtension Limit Switch Kit onboard filtering. No need for shielded wire.

    None of your schematics has any signal pull up either, capacitor alone won't help much.

    Don't mix Mains Earth and DC GND! Mains earth stays seperate at all times, don't use it for shielding either
     
  3. Trevor Farnum

    Builder

    Joined:
    Feb 15, 2017
    Messages:
    57
    Likes Received:
    10
    I have a very tight space, and at a different direction where the xtension switches won't work. Hence, the creativity. Inside a C-channel is the only place I could put it, on the z axis. Tight fit.

    Okay, how do I solve for this. I am sorry, not a electrical engineer.

    Where should it go? I don't have a mains earth in my shop. Would outlet ground work?
     
  4. Peter Van Der Walt

    Peter Van Der Walt OpenBuilds Team
    Staff Member Moderator Builder Resident Builder

    Joined:
    Mar 1, 2017
    Messages:
    14,868
    Likes Received:
    4,283
    To DC GND or a seperate Earth Spike. Not to the outlet, which is mains earth.

    Grbl Wiki has a basic schematic
     
  5. Trevor Farnum

    Builder

    Joined:
    Feb 15, 2017
    Messages:
    57
    Likes Received:
    10
    So, like this:

    Seems like I dont need the capacitor since you have the pull downs on the blackbox board. Correct me if I am wrong
     

    Attached Files:

  6. Peter Van Der Walt

    Peter Van Der Walt OpenBuilds Team
    Staff Member Moderator Builder Resident Builder

    Joined:
    Mar 1, 2017
    Messages:
    14,868
    Likes Received:
    4,283
    You do want the capacitor and resistor. Resistor 10k between SIG and V+. Capacitor 0.1uF across SIG and GND
     
  7. Trevor Farnum

    Builder

    Joined:
    Feb 15, 2017
    Messages:
    57
    Likes Received:
    10
    Like so:

    upload_2023-3-29_0-5-21.png
     
  8. Peter Van Der Walt

    Peter Van Der Walt OpenBuilds Team
    Staff Member Moderator Builder Resident Builder

    Joined:
    Mar 1, 2017
    Messages:
    14,868
    Likes Received:
    4,283
    Correct yes. Better than no filtering.

    Ideally at the switch though, not the near end of the cable. That's why Xtension switches runs on 3-core cable. To get V+ to the switch for the pull-up.
    At the Blackbox side, it has onboard RC+Opto filtering already.
     