Black box X32 probe issues
Discussion in 'Controller Boards' started by Joe hoffman, May 2, 2023.
  1. Joe hoffman
    I have upgraded a nema 17 Machine with the black box, I’ve done it once before with the x4, this time the probe won’t work.
    I keep getting:
    error: 9 - g code locked out during alarm or jog state [G4 P0.4]
    this error may just be a symptom of an earlier event:
    alarm:4 - probe fail. The probe is not in the expected initial state before starting probe cycle , where G38.2 and G38.2 is not triggered and G38.4 and G38.5 is triggered.
    I have checked all wiring, even unplugged the probe, unplugged my limit switches even.
    in the troubleshooting panel I can’t
    Make any of the inputs change state, so seems to be a disconnect there.
    1) Did you follow all the setup instructions in the BlackBox docs? Especially section 7.1 (read 7.2 as well) - up to date firmware is a must
    2) The Initial State issue could also indicate you haven't loaded a machine profile: either from the dropdown menu in Grbl Settings, or by restoring your Backup taken of the 4X using CONTROL > Grbl Settings backup settings / restore settings (CONTROL will apply needed changes for you, such as pin inversions, etc during the Restore process when you restore a 4X backup onto a new X32)
    The Inputs not reflecting in Troubleshooting is further evidence of (2) as well, as the profiles/restore would have set the report masks for you. If you didn't use the profiles, or a restore, and instead tried building the Grbl settings manually, some are incorrect at the moment (notable $6, $10 but possibly a lot of others too - better to use the tools than try to figure out the wrong ones one-at-a-time)
    With the above two tasks (firmware update and loading a machine profile) you should be up and running again.
    Also, the above mentioned tools - requires the latest version of CONTROL of course so make sure that's up to date too: v1.0.367 at the time of this reply - if not download from OpenBuilds Software: OpenBuilds CONTROL and OpenBuilds CAM
  3. Joe hoffman
    Yeah. Looks like my $10 bit mask was wrong, so that got my troubleshooting working, then I needed to invert the probe one. Now it seems I need a firmware update so trying to get python3 to symlink to python.
    Or just borrow a Windows machine for the quick update, Mac and Python paths can sometimes be tricky
